How to run 9.4 meters heat trace on a normal 3 inch pipe which is 1.4 meter long. 今天上班碰到一个问题。怎样把9.4米的heat trace Run在1.4 米的3寸管子上?) j9 b$ N: L( c# `& k
Detail:
9 T  {4 r6 n9 G0 GThe length of the heat trace is 22 meters.
( Z$ T1 l* C) q0 h* ]8 QAfter running heat trace through six valves. The rest of the heat trace is 9.4 meters.  
: v- ]3 b; }8 Z/ v0 P4 |  F3 dThese 9.4 meters heart trace can be run through the 1.4 meter 3 inches pipe ?
鲜花(0) 鸡蛋(0)
发表于 2010-7-5 22:20 | 显示全部楼层
本帖最后由 xdf 于 2010-7-5 23:49 编辑 2 d1 ~+ W+ n9 T/ F# A
8 s* X- J+ D5 y# {6 m0 ?2 j  @
在回答你的问题前,请问一下:
" L* c5 h; D- U( }前面的十几米是按要求的长度(尤其在阀门上,shoe上)铺设的吗?
7 y2 k! {% b( Q3 p8 T2 ]* `  C你的情况,是前面安装不妥,造成后面Cable太多,不符合设计要求,你需要重新按要求安装,而不是简单的挤一下。
7 x- r" {: V+ x' E# `: y. S9 [1 a+ B9 V  }0 l' j- C* c
从目前看,可能性:1。原来安装的不妥,重新安装
+ d( A. w3 [; z4 R2 ~0 ~6 ], o                  2。用错了TRACE,找到正确的,重新安装
/ s7 Y$ j; L- [0 s1 }. V                  3。设计失误,重新设计,ORDER,重新安装
鲜花(0) 鸡蛋(0)
发表于 2010-7-5 22:33 | 显示全部楼层
如果简单回答你的问题,3“管 要安 6个passes 不是不可能,要看radius
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-7-6 20:55 | 显示全部楼层
老杨团队 追求完美
3# xdf 1 w* a8 x  N3 G( T2 C8 d& _" P. M9 {
9 c! Z) H& j! E) T4 T

* M/ B& X2 w- w$ vThank you for your analysing. I agree it is designed problem. But What foreman concern is “can you finish ?”  Anyway it is possible. Today we figured it out. Today the soccer is worth to watch. we can talk about this question later
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-7-10 17:18 | 显示全部楼层
本帖最后由 jack_lai 于 2010-7-10 18:52 编辑
- I! |- O1 r5 N. |) J8 p" w1 ?7 A- W( j
1# jack_lai ' B! U, C3 f' R. q! a8 r
( [; ]0 W( \: h7 G8 c+ p
足球看完了来看看题目。$ f" y* E! n8 J  ?1 o; I0 b
8 B# E: I4 d: {+ l
The length of the heat trace is 22 meters. The size of the heat trace is 5/16 inch (WATTS/ m SUPPLIIED is 43.7)( f/ |. {: B: R+ M. z0 a1 f
The drawing is shown as figure 1. (All data is from the memory.  They are not the same as the real drawing, but a little bit different)
/ \% n9 C  W. a% p4 }9 e' KWe can see it is not easy to install the 22 meters heat trace according as figure 1' j$ B/ ^7 S3 b( \

+ O. p! A6 U/ V' F1 P$ L( E DSC051241.jpg 4 K( a: L* \5 ~% a4 G
, I. j7 k2 f( E9 H7 s" p
. b: I9 h) r+ M; \! z) j/ q
As a normal question we just discuss:
, V, k; c( X! L$ i' S. m' YHow do you run these 9.4 meters heat trace (size 5/16 inch) on the 3 inches 1.4 meters pipe ?
& d- @: Y0 h5 i) {I call this is JACK LAI Spiral Method 螺旋法
" ~; Y5 u" e  U1 Q; C. h4 g. N. rThe outside circumference of the 3 inch pipe is more than 10 inches.  See figure 2.
. i* u/ @. k& PThere are 10 positions to plac the heat trace. They are 0.1,2,3,,,,,9.  The distance between each position--heat trace is about one inch. 5 l' L% x8 y: Y* k  K" A* ]+ Z7 Y
Because the pipe is horizontal, position 0 can not be placed. See figure 22 L- Q: S# a- f; n
Because the maximum bend radius of the heat trace is 2 inches( see note 1),  position 5 can not be placed. See figure 2. Then the route of the heat trace can be like figure 3  L! e! Y& u. d$ F
The total heat trace that can be installed here is about 7 B# a" D+ g( ]  l# @
1.4 * 6 + 1 * 2 = 8.6 + 2 =10.8 Meters
$ o  L8 W: z1 y0 w9 ~9 XSo, the 9.4 meters heat trace can be installed along the 3 inched 1.4 meters pipe without a problem.
% k) v4 X6 k7 y/ V# O: W, |$ S8 H+ y4 N$ @/ v( e9 G) X. L
Note :
! q. N7 _, g( W9 W1. The minimum bend radius:
) q* H- U: M4 \7 q8 t* T; pBecause the heat trace size here is 5/16,  6 times the outside diameter of the heat trace is8 ~: u# j; C* O% i
5/16 *6 = 30/16 almost = 2 inches
' j+ m2 R* q, f% m: `/ j+ n( {/ \1 J$ hSo the maximum bend radius is 2 inches.
, `" d' a4 H- T+ D% p/ W6 P( T8 v5 z; R% k3 E$ W
DSC051251.jpg
" s+ w' N( L  k
, \! L% |! B! V/ ]5 y: l" sSummary
/ {3 a% j# Y# OAs regular
4 @, d# {/ x6 Y# n; i& h5 aFor 3 inch pip: If heat trace size is 5/16 inch, and no RTD, the box position is close to the end of pipe. 1 meter long pipe
) I% Y6 b# i2 Z& e( \if the pipe is horizontal, The length of heat trace can be installed is about1 g8 Q$ s7 h: K2 [9 _+ f
1 * 9 = 9 meters
3 A! x# C; B+ P$ R, fIf the pipe is vertical, The length of heat trace can be installed is about
& f& D9 @9 S) ?& h/ }$ i1 * 10 = 10 meters. ; H( u+ D% ^* s
For 2 inch pipe: If heat trace size is 5/16 inch, and no RTD, the box position is close to the end of pipe. 1 meter long pipe0 i# l' l- l; g  K, F; \  i
if the pipe is horizontal , The length of heat trace can be installed is about' \) v2 S  o4 e1 b" O' `2 g
1 * 4 = 4 meters7 A7 r, x8 f4 y
If the pipe is vertical, The length of heat trace can be installed is about' h; D: @- D; H. J7 J4 ~
1 * 5 = 5 meters.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-7-10 19:49 | 显示全部楼层
5# jack_lai : @8 ^6 {: Y# V7 l0 N

( r1 W- j- ^; k1 d7 ]2 c; F9 l  H3 b8 B* d4 }, t
"if the pipe is horizontal, The length of heat trace can be installed is about* T: z- p0 E0 o2 g7 X1 P
1 * 9 = 9 meters
% w8 h1 @" B( o  @If the pipe is vertical, The length of heat trace can be installed is about
' ]* L& m  O9 X* v7 W6 f6 ~1 * 10 = 10 meters. "/ t: E+ {" {/ B5 T) ^
应该改成
5 q4 z8 D4 q2 Z" E( ?. m" `6 Aif the pipe is horizontal, The length of heat trace can be installed is about
9 C! m0 w( j# B/ q6 W4 w: @1 * 8 = 8 meters
3 R5 ]# o3 L& s7 |If the pipe is vertical, The length of heat trace can be installed is about4 z; e! U+ O2 f9 D1 H
1 * 9 = 9 meters.
- R( c& A( c3 U/ t- Z, ?1 q6 X; |- O如果你把heat trace 的间距再调小些,上面的公式有可能成立.
鲜花(0) 鸡蛋(0)
发表于 2010-7-15 22:51 | 显示全部楼层
老杨团队,追求完美;客户至上,服务到位!
Good job!# v  V3 c2 z! P$ J6 S" r
Another way, you can put the extra trace on the 3' valve if it have room.5 \" y0 _- N  f2 K# p/ R; k
The last way, you can burn(install) the extra trace on next pipe which connected to your pipe.
鲜花(0) 鸡蛋(0)
发表于 2010-7-23 20:53 | 显示全部楼层
建议问现场的manufacture 它们最权威,,, 别自己做主,,,这条trace 有问题...